wiring house in douglas county co
buddhakii
Littleton, CO
Does anyone here wire houses in Douglas County Colorado? Just got my rough done today and the inspector mentioned I need shower trims on the can lights in all clothes closets no matter how far away from storage I am. The cans are all CFL's.
Inspector
Inspector
As per Art,410.8 if the recessed cans are incandescent fixture then it would need to be of the totaly enclosed type if all the fixture will accept is a florescent type bulb then by the NEC it would not be required. But Douglas County is there own jurisdiction so you may want to just comply
This may seem like a stupid question but, are the cans rated for a shower trim I believe some of them are not ( the CFL type cans ) not that they will not work but the listing is not there. Elco comes to mind as one that may not be listed for use with a shower trim and fluorescent lamp.
Seems your on NEC 2005 and 2003 International Building Code, based on this Page based on this page.
www.Douglas.co.us/community/building.
I did find a page in there that stated they took the total NEC 2005 with out amendment.
You are a candidate for their newsletter! :rolleyes:
Maybe some of it will help.
Don't know about your area, but in my area I had to have a globe or a lens for a closet light, no open bulbs, no matter if they are fluorescent.
Where is "just south of Baltimore"?
I have used open-tube fluorescent in every jurisdiction around here with 0 issues from inspectors. :confused:
closet lights
closet lights
John, I can only say in the counties I've worked in they have always (since '02 I think) required closet lights to have a globe or a lens. Speaking resi. of course. I live in Millersville, hence the "just south of Baltimore".
Where are you located?
Welp, seems that would be violation of Article 410.8(C), 2005' ; 410.16, 2008'.
Open tube fluorescents are allowed in closets providing your have the clearances needed.
Back to the OP-- if this can is a PLC type CFL then the inspector is incorrect in requiring a lens for the closet howwever, depending on the situation he may be correct in citing a violation in the shower.
Let's go with the CODE! I never said they weren't allowed, the OP I was addressing and stated "open tube", now I'm thinking an open tumb stone and not fully enclosed. 08 clears alot of this up...
I don't get it... open tube is a fluorescent strip light, as an example. It is perfectly OK -- not sure what the 08 clarified
Baltimore (Catonsville). And I have done a lot of work in Anne Arundel county.
Gotta disagree. There is no requirement for a fluorescent to have an enclosed lamp.
If the can is listed as a "recessed fluorescent luminaire" then it may be installed in a clothes closet, 410.16(A)(2). There is no NEC requirement that the lamp be enclosed if it is listed as such.
410.16(C)(4) indicates the can should be no closer than 6" to the storage space inside the closet.
That's exactly how I inspect them.
Enjoy your day off, George. I'm working. :smile:
If you want to say that a surface mount light could not a flourscent light, & my arguement is open tub (not enclosed) well keep doing what you know! 410.16 ALL