Hello.
I helped a friend over the phone to trouble shoot his hydronic radiant heat which wasn't getting hot. He was emailing me photos and I talked him through it.
He has a boiler with 8 honeywell zone valves for base board heat. Off the boiler he has a separate zone valve with a separate circulator pump and a Honeywell RA832A dpst relay for the radiant heat with a mixing valve.
My question, in the RA832A there is a T T which goes to the areas thermostat. There is also an X X which is an auxiliary contact which I'm gathering goes back to the T T on the boilers Aqua-stat ( I didn't ask him for pictures of the inside of the Aqau-stat)
If any of the 8 baseboard zones are energized, the end switch makes, the boilers circulator pump comes on and the boiler will heat up if needed.
If the radiant heat zone is energized the radiant heat circulator comes on and the X X terminals send power back to the aqua-stat T T terminals (I'm gathering) to control the boiler.
What about the circulator pump on the boiler?? Besides the boiler being energized so will the boilers circulator pump even though there's no boiler baseboard zones open.
Is this correct?
I helped a friend over the phone to trouble shoot his hydronic radiant heat which wasn't getting hot. He was emailing me photos and I talked him through it.
He has a boiler with 8 honeywell zone valves for base board heat. Off the boiler he has a separate zone valve with a separate circulator pump and a Honeywell RA832A dpst relay for the radiant heat with a mixing valve.
My question, in the RA832A there is a T T which goes to the areas thermostat. There is also an X X which is an auxiliary contact which I'm gathering goes back to the T T on the boilers Aqua-stat ( I didn't ask him for pictures of the inside of the Aqau-stat)
If any of the 8 baseboard zones are energized, the end switch makes, the boilers circulator pump comes on and the boiler will heat up if needed.
If the radiant heat zone is energized the radiant heat circulator comes on and the X X terminals send power back to the aqua-stat T T terminals (I'm gathering) to control the boiler.
What about the circulator pump on the boiler?? Besides the boiler being energized so will the boilers circulator pump even though there's no boiler baseboard zones open.
Is this correct?