NMC is allow UF is not, Non of them is allowed Embedded in poured cement, concrete, or aggregate.B) Type NMC. Type NMC cable shall be permitted as follows:
(1) For both exposed and concealed work in dry, moist, damp, or corrosive locations, except as prohibited in 334.10(3)
(2) In outside and inside walls of masonry block or tile
(3) In a shallow chase in masonry, concrete, or adobe protected against nails or screws by a steel plate at least 1.59 mm ( in.) thick and covered with plaster, adobe, or similar finish