Wiring in parking structure slabs
steve holt
Hawaii
Is there a difference between running wiring in a raised slab that has vehicular traffic and wiring within a slab on grade with vehicular traffic. My opinion is that there is no difference as long as the wiring is physically within the slab on grade. If however the wiring is below the slab on grade, then I would have to follow the requirements of 300.5.
300.5 agrees with you.
300.5 Underground Installations.
(A) Minimum Cover Requirements. Direct-buried cable
or conduit or other raceways shall be installed to meet the
minimum cover requirements of Table 300.5.