We are providing consulting/engineering services for an industrial client for a new facility. They want to run the power from the electrical room out to the production lines and throughout the production lines in a "trench" system. We have figured out that what they are talking about is a fairly large trench formed into the concrete floor with cable tray(s) in it and a metal cover. We have never come across this before, but the client insists they have seen it and it is what they want. We can come up with MANY reasons not to do this but they cannot be convinced that this is not a normal way to power production equipment. For the most part the production process is dry so water/moisture in the trench will not be a normal thing. Our concerns are how dirty the inside of the trench will get, fork truck traffic over the trench, how to get the wiring out of the trench to control panels and production equipment, how to make the bends in the cable tray (the sweep of a 90 degree bend will make the trench huge).
We have done code review and cannot find any reason to say that it violates code.
Does anyone out there have any experience in this type of application? Have ideas or recommendations for us? We have extensive experience in industrial facilities, but have never come across installations like this.
We have done code review and cannot find any reason to say that it violates code.
Does anyone out there have any experience in this type of application? Have ideas or recommendations for us? We have extensive experience in industrial facilities, but have never come across installations like this.