DataCenterGuy

Member
Location
New York
Is it legal to wire an L14 Receptacle to 2 Phases + Neutral of a 3-Phase Circuit? I've always understood an L14 to be for 3-Phase + Ground, and L21 to be used when both 120V and 208V services are required.

The only thing I can find in the Code is 406.3 (F) which I read as precluding this usage if L14's are also used elsewhere on the premises for 3-Phase (No Neutral) service.

If 2-Phase + Neutral connection to an L14 is permitted, would it need to be identified?
 
My default answer would be to check the listing of the device but there might be some other prohibition.
 
L14 = 125/250 L1, L2, N, G
Your first description would be the proper way to connect it. It is not a 3 phase configuration.
 
Thanks! Case Closed !

Thanks! Case Closed !

I agree. The OP may have seen the NEMA description of 3-P 4-W. The P is for pole not phase.

Thanks for pointing out the obvious that I should have seen myself. Amazing you can get stuck in a through :ashamed1:rut and overlook what's staring you in the face!
 
Is it legal to wire an L14 Receptacle to 2 Phases + Neutral of a 3-Phase Circuit?
This is relatively common in datacom and temporary power setups. Most of these actually run two sets of 120V loads, but a few actually utilize both voltages.

There is some truly ancient 240V equipment will balk at 208V (not our problem) and of course the 25% hit that resistance heating suffers.


I would cite 110.3(B).
It sounds like a good way to single phase a three phase machine equipped with an L-14P

If someone wires a three-phase machine to an L-14P, they deserve what they get. The same idiot could just as easily wire something to a 347/600 plug.

I prefer to use L21 receptacles and then manage phase balance by wiring the cords differently, but there is nothing inherently unsafe about using an L14 device in this configuration.
 