I have been seeing this wiring method used in alot of the new homes being built in Northern VA.
Two 15A circuits being fed from the panel via a 14/3 wire.
An example would be that the 14/3 would run to a room. The black wire would power the lights and the red would power receptacles.
I know a common neutral is allowed, but using 14AWG, isn't the ampacity only 20A (table 310-16)?
Isn't the potential for 30A to be on that neutral without the breakers tripping?
Thanks.