I'm a residential guy, but have volunteered to do an HVAC install for my church and need a little help from you commercial guys. Here's the situation.....
Installing 7 Mitsubishi ductless mini splits in the classroom areas of a ca.1930 building. One of the rooms can potentially hold 100 people, so I am planning to follow code for a place of assembly, even though it might be debatable since this is a classroon. All wiring (whether pipe, MC, etc.) will be surface mounted or enclosed in a plastic "line hide" with the refrigerant lines and condensate drain hose. The main challenge is complying with both a wet rated method and a place of assembly method. The wiring between the indoor and outdoor unit is composed of 3 conductors, S1, S2 and S3, plus a ground. S1-S2 is 208/230, with S2-S3 being a 12-24 VDC pulse signal for control. Recently attended their factory install class, in which they are adamant that S1-S2-S3 conductors CANNOT be spliced ANYWHERE between the units. They must be 14AWG, no bigger, no smaller, and can be stranded or solid. They say the communication portion of the circuit can be affected by wire size and splicing, thus their stance. As I see it, I have a few options:
1. Use a PVC coated MC (TECK) cable for a continuous run. Deal with the expense/availability of wet rated connectors outdoors.
2. Use sealtite or NM conduit outside to a JB just inside the interior wall, where the remaining run will be EMT or FMC. Wire with continuous THWN.
3. Use MC for the interior run and NM conduit/sealtite for exterior. Making sure the MC wire is THWN, remove the MC jacket for the portion of wire that needs to be in the conduit/seatite and transition it in a JB just inside the exterior wall.
I seem to be leaning toward option 3. Our church is on a very tight budget, so cost is a major factor. Other ideas/issues?
Installing 7 Mitsubishi ductless mini splits in the classroom areas of a ca.1930 building. One of the rooms can potentially hold 100 people, so I am planning to follow code for a place of assembly, even though it might be debatable since this is a classroon. All wiring (whether pipe, MC, etc.) will be surface mounted or enclosed in a plastic "line hide" with the refrigerant lines and condensate drain hose. The main challenge is complying with both a wet rated method and a place of assembly method. The wiring between the indoor and outdoor unit is composed of 3 conductors, S1, S2 and S3, plus a ground. S1-S2 is 208/230, with S2-S3 being a 12-24 VDC pulse signal for control. Recently attended their factory install class, in which they are adamant that S1-S2-S3 conductors CANNOT be spliced ANYWHERE between the units. They must be 14AWG, no bigger, no smaller, and can be stranded or solid. They say the communication portion of the circuit can be affected by wire size and splicing, thus their stance. As I see it, I have a few options:
1. Use a PVC coated MC (TECK) cable for a continuous run. Deal with the expense/availability of wet rated connectors outdoors.
2. Use sealtite or NM conduit outside to a JB just inside the interior wall, where the remaining run will be EMT or FMC. Wire with continuous THWN.
3. Use MC for the interior run and NM conduit/sealtite for exterior. Making sure the MC wire is THWN, remove the MC jacket for the portion of wire that needs to be in the conduit/seatite and transition it in a JB just inside the exterior wall.
I seem to be leaning toward option 3. Our church is on a very tight budget, so cost is a major factor. Other ideas/issues?