Wiring method Optometrist office
john h
Would an Optometrist's office (not an Opthamologist)fall under patient care Article 517.13(A)? I understand no to hospital grade receptacles or isolated ground but what about redundant ground? As always, thanks for the help.
Re: Wiring method Optometrist office
John
Look at the definitions under 517.2 and in particular Health Care Facilities. I do not see
Optometrist's offices listed.
[ January 22, 2004, 12:13 PM: Message edited by: bob ]
That definition is not restricted to that list. In the paragraph above that it states medical - is an optometrist in the medical field? I would be very careful in categorizing this space, They use a lot of specialized equipment with chairs not much different than dentists.
Pierre
In Washington State, health care facilities require a plan check by the AHJ prior to the job starting. Have you considered asking your AHJ if this is required a health care facility.
Thank you everyone for responding. We checked the internet for the definition of an optometrist and found that he or she is, in fact, a medical doctor capable of performing detailed examinations int the office. Our conclusion was, therefore, that redundant ground was required but that hospital grade recepticals were not. Thanks again for the input.
An IG ground, IMO, serves no usefull purpose. I don't see why not, assuming proper permits and inspections are done as required.
Tom, thanks, i was just checking to see if i had violated any code.Not an area i usually am involved in.Inspection is not something i care to talk about in here as it draws to many disagreements :p