Its not on the ground its on the edge of the slab, so very similar to running along the foundation of a building.Conduit isn’t allowed to run on the ground surface, except under a building, generally. Except for rigid.
You would have a hard time complying with the fastening requirements with it laying on the ground.
And I would say it is subject to physical damage as well.
I would think it needs to be buried 18” minimum.
At that point just run PVC.
I hope it's legal. I recently did the exact same thing, except I undercut the dirt below the concrete, so the LFNC I ran (with UF in it) is actually under the edge of the pad, instead of next to it.