electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
- Occupation
- Electrician
I have to come out of a 2000A switchboard, theu a CMU wall to a 2000A transfer switch outside. There is about 10-12 feet between the wall and the transfer switch. There is already a large box mounted on top of the switch board. The equipment is oversized, with 3 years of demand data showing max demand of 136KW. (377A). Thus i will probably reduce the feeder down to maybe 1200A. I can probably get 2 sets of 600Al in a 4" with a reduced neutral, in which case that would be 4 conduits total (2 out, 2 back in). We're just toying with other options. What about using a 3r wire way? I can just cut a hole in the CMU wall, use a wire way and box flange to come into the back of the inside box, then nipple put the bottom into the top of xfer switch. Another option might be cable tray, but that doesn't seem like a great option due to transitioning from inside to outside and having to go into the top of the switch. Any other thoughts or ideas? Should I just run the conduits?