Wiring Method

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Surface mounted and EMT must be used. Would there be any issued dropping doen one 3/4" pipe and nipple between boxes? I think (3) sepaparte conduits doen from ceiling would be foolish. No derating issues. 6 CCC's conductors.

1722969265484.png
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
What's the wire size(s), and where is the other end going?

If this is a home run, almost certainly one conduit.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
We do it all the time.
One item we do is pull long enough so there is no splices in any box other then the EGC.
4 and 6 is pulled thru 2, no splice.
6 is pulled thru 2 and 4, no splice.
Helps with box fill as well.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
While generically It would be acceptable to run in one conduit, There are many situations that would make such not advisable and maybe even not allowed. The limited information contained in OP post as well as on image of plans really has insufficient to give a definitive yes or no to your question.
Information such as: Are the 3 circuits coming from a single trough box or already in separate runs? Are these circuits generated from different sources characteristics or different panels? You mention using nipples to connect 3 boxes, would the enclosures involved create a fill issue with the pass through conductors and any respective devises installed? If coming down into a typical handy box (used a lot to give a lower profile and rounded edges) and switch or receptacle, box fill become a real issue for pass through.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Also pay close attention to the project specifications...they may specify individual conduits for each circuit.
 