Went to a service call at the end of the day today,
Cable line from a TV had touched a forced hot water base board heater and cause quite an arc. Did not trip any breakers.
The house is wired kind of funky BX turns to romex... no j-boxes to be found.
Pluged in a outlet tester and it reads open ground. Opened up the box and neutral in reading Hot. Besides it being reversed everything rings up okay with a voltage tester.
Now...
We go to another room with a different circuit and it reads open ground..... but when we go to the other room and connect the neutral which is(hot) to ground the circuit read correct.
Voltage readings we kinda all over the place on the cable 60v , 120v , 150v on the cable to ground
Any ideas
Thanks
bob