wiring requirements Article 517
Are the wiring and protection requirements of patient care areas (specifically examining rooms in doctor's offices) new in 2008?
Where can I find the definition of "patient care areas?
Take a look at the definition of patient care area in 517.2.
Which requirements are you specifically asking about?
The requirements for patient care areas has not be significantly changed in the 2008 NEC.
By the way welcome to the forum.
Chris
patient care is defined in 517 (pgs 426,427)
There were some changes, but none that jump out that would be classified as "major" IMHO
Along with Chris and Augie's posts,
Patient Care Area. Any portion of a health care facility wherein patients are intended to be examined or treated. Areas of a health care facility in which patient care is administered are classified as general care areas or critical care areas. The governing body of the facility designates these areas in accordance with the type of patient care anticipated and with the following definitions of the area classification.
FPN: Business offices, corridors, lounges, day rooms, dining rooms, or similar areas typically are not classified as patient care areas.
General Care Areas. Patient bedrooms, examining rooms, treatment rooms, clinics, and similar areas in which it is intended that the patient will come in contact with ordinary appliances such as a nurse call system, electric beds, examining lamps, telephones, and entertainment devices. [99, 2005]
Critical Care Areas. Those special care units, intensive care units, coronary care units, angiography laboratories, cardiac catheterization laboratories, delivery rooms, operating rooms, and similar areas in which patients are intended to be subjected to invasive procedures and connected to line-operated, electromedical devices.
Wet Procedure Locations. Those spaces within patient care areas where a procedure is performed and that are normally subject to wet conditions while patients are present. These include standing fluids on the floor or drenching of the work area, either of which condition is intimate to the patient or staff. Routine housekeeping procedures and incidental spillage of liquids do not define a wet location.
Roger