Hi
We are selling a computerized lighting controller, and I want to make sure my information is correct. The idea is to show a before and after having added the lighting controller. This controller operates at line voltage (100 to 277 VAC). It is rated:
Figure 1: Before
Figure 2: After retrofit.
This lighting controller (slave device) is networked together with a number of other controllers (including a master) and to wall devices through the "To / From Subnetwork" cabling. This cabling is standard Cat 5e network cable (with RS-485 data communication running through it). The control inputs (for the light switch) are low-voltage signalling dry-contact inputs (0-3.3 VDC).
Here are my questions:
1) Can the low voltage Cat 5e network cable be in the same enclosure without a barrier separating the low and high voltage sections? This is expensive and we would like to avoid this.
2) Will the Cat 5e network cable have to be rated as UL 444 making it suitable for 300 Volt applications? Otherwise, what cable should be used?
3) Can the Cat 5e network cable be installed outside of a conduit if it is FT-6 plenum cable, using appropriate methods (for example, keep the cable off of the ceiling tiles)?
4) Is it OK to reclassify the circuit for the control input? See NFPA 70, 300.3.(C)(1) in the context of a class 2 circuit that has been reclassified as a class 1 circuit [725.130(A) Ex2]. Is the control input circuit considered to be a class 2 circuit?
Thanks for your help!
We are selling a computerized lighting controller, and I want to make sure my information is correct. The idea is to show a before and after having added the lighting controller. This controller operates at line voltage (100 to 277 VAC). It is rated:
- UL Listed (CDN & US) UL 61010-1 Safety Requirements For Electrical Equipment For Measurement, Control, And Laboratory Use - Part 1: General Requirements - Edition 2 - Revision Date 2008/10/28
- CSA C22.2 NO. 61010-1 Safety Requirements For Electrical Equipment For Measurement, Control, And Laboratory Use - Part 1: General Requirements - Edition 2 - Revision Date 2008/10/01
Figure 1: Before
Figure 2: After retrofit.
This lighting controller (slave device) is networked together with a number of other controllers (including a master) and to wall devices through the "To / From Subnetwork" cabling. This cabling is standard Cat 5e network cable (with RS-485 data communication running through it). The control inputs (for the light switch) are low-voltage signalling dry-contact inputs (0-3.3 VDC).
Here are my questions:
1) Can the low voltage Cat 5e network cable be in the same enclosure without a barrier separating the low and high voltage sections? This is expensive and we would like to avoid this.
2) Will the Cat 5e network cable have to be rated as UL 444 making it suitable for 300 Volt applications? Otherwise, what cable should be used?
3) Can the Cat 5e network cable be installed outside of a conduit if it is FT-6 plenum cable, using appropriate methods (for example, keep the cable off of the ceiling tiles)?
4) Is it OK to reclassify the circuit for the control input? See NFPA 70, 300.3.(C)(1) in the context of a class 2 circuit that has been reclassified as a class 1 circuit [725.130(A) Ex2]. Is the control input circuit considered to be a class 2 circuit?
Thanks for your help!