Hi there,
I have overcurrent question about circuit breaker. I have been using the rule of thumb for continuous load where if it is a fuse I size the size of the fuse to 125%, and if it is a ckt. brkr, I size to 150%.
Of course i could not find anythign about the 150% for ckt brkr. So i would like to revise this rule I knew.
1) Typically, do i size to 125% or 150% or more for a circuit breaker?
2) What is it is for a adjustable circuit breaker?
3) What is it is for a fixed circuit breaker?
4) I don't understand this phrase. Does it mean if i have a standard rating of a fuse and fixed circuit breaker, the 125% does not apply ? what is a standard rating of a fuse mean as well?
"Where 125% of the primary current doesn't correspond to a standard rating of a fuse or nonadjustable circuit breaker as listed in 240.6(A), the next higher rating in Table 450.3(B) is acceptable (Note 1)."
5) If i have a transformer of 250kVA, where the primary is 480VAC, and secondary 400Vac with a fixed and or adjustable circuit breaker of 400Amps, what do i size my primary wire going into the transformer and going out of the transformer? Based of the NEC Ampacity chart of 90°C (http://www.usawire-cable.com/pdfs/nec%20ampacities.pdf)
From my calcs:
Primary : 300.71 Amps (250,000 / 480 / 1.732)
Primary x 125% : 375.89 Amps
Secondary : 360.85 Amps (250,000 / 400 / 1.732)
Secondary x 125% : 541.28 Amps
Hope to hear from everyone!
I have overcurrent question about circuit breaker. I have been using the rule of thumb for continuous load where if it is a fuse I size the size of the fuse to 125%, and if it is a ckt. brkr, I size to 150%.
Of course i could not find anythign about the 150% for ckt brkr. So i would like to revise this rule I knew.
1) Typically, do i size to 125% or 150% or more for a circuit breaker?
2) What is it is for a adjustable circuit breaker?
3) What is it is for a fixed circuit breaker?
4) I don't understand this phrase. Does it mean if i have a standard rating of a fuse and fixed circuit breaker, the 125% does not apply ? what is a standard rating of a fuse mean as well?
"Where 125% of the primary current doesn't correspond to a standard rating of a fuse or nonadjustable circuit breaker as listed in 240.6(A), the next higher rating in Table 450.3(B) is acceptable (Note 1)."
5) If i have a transformer of 250kVA, where the primary is 480VAC, and secondary 400Vac with a fixed and or adjustable circuit breaker of 400Amps, what do i size my primary wire going into the transformer and going out of the transformer? Based of the NEC Ampacity chart of 90°C (http://www.usawire-cable.com/pdfs/nec%20ampacities.pdf)
From my calcs:
Primary : 300.71 Amps (250,000 / 480 / 1.732)
Primary x 125% : 375.89 Amps
Secondary : 360.85 Amps (250,000 / 400 / 1.732)
Secondary x 125% : 541.28 Amps
Hope to hear from everyone!