Hello All,
Because of space limitation, the 800KVA UPS will be installed 20ft away from the battery cabinet.
Can I size the wires for this DC connection just like AC using NEC Table 310.16 (NEC 2008 and before) or 310.15 (NEC 2011)?
Thanks.
 

Carultch

Senior Member
Location
Massachusetts
Hello All,
Because of space limitation, the 800KVA UPS will be installed 20ft away from the battery cabinet.
Can I size the wires for this DC connection just like AC using NEC Table 310.16 (NEC 2008 and before) or 310.15 (NEC 2011)?
Thanks.

Ampacity is valid for both AC and DC.
Voltage drop has a specific table in Chapter 9 for each version. I think Table 8 is DC, and Table 9 is AC, if I remember correctly. And for AC, it depends on conduit material.

Voltage drop could be significant, given low nominal operating voltage.
 
Last edited:

broadgage

Senior Member
Location
London, England
You may need wire much larger than the minimum permitted by code. UPS systems are often very sensitive to voltage drop in the battery circuit, and you may need to limit this to 1%, rather than the commonly accepted figure of 3%.
 