mtnelectrical said:
... this is an outdoor unit, and when is required to fused?
The unit is only required to be fused if the dataplate specifically says "maximum fuse size...." instead of "maximum fuse or breaker size". If it says fuse only, the typical place to accomplish that would be by way of a fused disconnect.
 
woulld it still need disconnect on top of unit or it could in sight of unit 50' away or less?
Look at 440.14 and the definition of readily accessible. In my opinion it must be on top of the unit as it must be "readily accessible" from the refrigeration equipment.
 