I spent a couple hours in a mansion I got called out to and am going back tomorrow. Customer has lived in house for 13 years with no problems. Last Saturday, half their partially finished basement suddenly went out (lights and outlets). It appears that everything that went out is on one circuit. There was no event that triggered this! No other tradesmen in the house. Just two wealthy sisters and their children. 90% of the portion that went out isn't in use. The part that is has a TV and an XBOX plugged in. Although there's 23 lights and 20 outlets that are out, still appears to be one circuit in an unoccupied part of the basement.
It's a very loaded up Eaton 200 Amp panel pushing 40 A on each leg, which is fine. No breakers are tripped though. I plugged the Klein plug tester/ tracer-signaler into two different outlets that were off. Both traced back to the same circuit breaker. This breaker rang out fine with a multimeter. 120V on the load side. Maybe I have to test the load side of every breaker. It's like 48 slots with multiple tandems. I'm thinking it's either an open hot somewhere or a GFCI that's wired wrong. Would a Circuit Tracer work properly under these conditions?
The work done in this place is immaculate despite 3 neutrals landed under 1 screw every time! Done simply to make it look pretty! 2/3 of the Neutral Bars are empty! The ground bars are done this same way. However the section that's out was done by a family member 10 years ago and isn't original. Over the phone, after I left, he claimed that the circuit is marked correctly (#15) (which is not the one that I'm tracing out (#44)). The circuit that I'm tracing out also has a $7,000 chandelier on it that is working, along with a couple can lights that surround it. I'd like to avoid having to open the first floor devices up if I can so I'm questioning if I'm tracing the right circuit in the first place.
It's a very loaded up Eaton 200 Amp panel pushing 40 A on each leg, which is fine. No breakers are tripped though. I plugged the Klein plug tester/ tracer-signaler into two different outlets that were off. Both traced back to the same circuit breaker. This breaker rang out fine with a multimeter. 120V on the load side. Maybe I have to test the load side of every breaker. It's like 48 slots with multiple tandems. I'm thinking it's either an open hot somewhere or a GFCI that's wired wrong. Would a Circuit Tracer work properly under these conditions?
The work done in this place is immaculate despite 3 neutrals landed under 1 screw every time! Done simply to make it look pretty! 2/3 of the Neutral Bars are empty! The ground bars are done this same way. However the section that's out was done by a family member 10 years ago and isn't original. Over the phone, after I left, he claimed that the circuit is marked correctly (#15) (which is not the one that I'm tracing out (#44)). The circuit that I'm tracing out also has a $7,000 chandelier on it that is working, along with a couple can lights that surround it. I'd like to avoid having to open the first floor devices up if I can so I'm questioning if I'm tracing the right circuit in the first place.