I'm wiring a pole barn and running 3/4 conduit and metal boxes . The beams are 8 feet apart and I mounting a box on every other one, 3 screws per box. Do I still need to support conduit within 12". There is nothing to support to.
What kind of conduit? Several types require the support within 3' of the box.
3/4 EMT
358.30 Securing and Supporting. EMT shall be installed as a
complete system in accordance with 300.18 and shall be
securely fastened in place and supported in accordance with
358.30(A) and (B).
(A) Securely Fastened. EMT shall be securely fastened in
place at intervals not to exceed 3 m (10 ft). In addition, each
EMT run between termination points shall be securely fastened
within 900 mm (3 ft) of each outlet box, junction box, device
box, cabinet, conduit body, or other tubing termination.
Exception No. 1: Fastening of unbroken lengths shall be permitted to be
increased to a distance of 1.5 m (5 ft) where structural members do not
readily permit fastening within 900 mm (3 ft).
3' is the general rule but there is this exception
Use box support brackets this can be mounted to the box before it is installed
They technically meet code, reality is the raceway likely is supporting the strap more so than the strap is supporting the raceway.We call them Fake Caddys or Miracle Bars. I have no idea how those things are legal but we have been slapping them in everywhere.