I am calling this a hazard regardless, but am I also correct that this violates 406.8?
T tonype Senior Member Location New Jersey Jun 2, 2021 #1 I am calling this a hazard regardless, but am I also correct that this violates 406.8?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 2, 2021 #2 Violation every time. 406.9(C) Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall. Click to expand...
Violation every time. 406.9(C) Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall. Click to expand...
petersonra Senior Member Location Northern illinois Occupation engineer Jun 2, 2021 #3 Is it a GFCI? If so what would the hazard be.
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety Jun 2, 2021 #4 petersonra said: Is it a GFCI? If so what would the hazard be. Click to expand... We can debate the hazard, but 406.9(C) seems pretty clear that it's a "no-no."
petersonra said: Is it a GFCI? If so what would the hazard be. Click to expand... We can debate the hazard, but 406.9(C) seems pretty clear that it's a "no-no."