TrickleCharge
Member
- Location
- CA
So i have a woodworking shop that is going to also install dust collector. The hazardous/classification report states that with all the woodworking equipment, the dust collector will work to "declassify" the area along with good housekeeping. Now with NFPA 499 5.4.1 this is true to unclassify a location on the basis of a dust removal system that prevents dust clouds and lay accumilations that make surface colors indiscernible. Or you can unclassify an area on the basis where excellent housekeeping prevents the same result as the dust collection system. My question is....how do i know that the dust collection will do such if the manufacturer has no proven data or samples that can support the conlusion that the dust is greater than 420 microns (Fire Code Def. of Combustible dust is dust smaller than 420 microns) or can mitigate the dust with the equipment installed to a point that would declassify it. So basically they say "well we have a dust collection system why do we need a classifation study?" But Im wondering where is the evidence that supports this claim? Any input?
Thanks