Greg1707
Senior Member
- Location
- Alexandria, VA
- Occupation
- Business owner Electrical contractor
I swapped out a panel in August. There was a 30 amp double pole GFCI breaker feeding a hot tub heater. These breakers are not available. I am number 597 on the list of people waiting for a Homeline breaker. 40 amp spa disconnects with GFCI protection however are available. Would it be permissible to replace the existing non fused spa disconnect with the 40 amp GFCI disconnect? The conductors will be protected by the 30 amp breaker in the panel.