We have a panel installed in a closet. The closet door width is 36? wide, panel width is 20?. Front of panel is parallel to the closet door when the closet door is closed. Distance from inside of closet door to front of panel is 24?. Door on panel can fully open 90 degrees with the closet door open or closed.
With the closet door open, you have the 30? width and more than 48? in front of the panel. Panel is 120/208 3 phase 100 ampere panel.
Does this install violate 29CFR1910.303(g)(1)(vi)(B) of the OSHA regulations(basicly, NEC 110.26(A)(1)? There is no AHJ other than OSHA for this location.
Assume the closet is not used for any other purpose, i.e. no mops, buckets, etc.
Thank you for your comments.