Working / clear space above panelboard ?

Status
Not open for further replies.

ritelec

Senior Member
Location
Jersey
New work. 200amp service. I noticed yesterday that the AC guy put a duct and the plumber a pex pipe right over the area where I plan to place the panel

Working space shall be 6.5 above floor or height of equipment which is ever greater.

The space is 30" x 36"

I believe the clear area above the panel extends 6' up from the top of the panel.

Looking sideways at the panel (so you're looking at the 36" working space depth in front of the panel)

Does the area that no foreign equipment can be in extend up from the face of the panel ( and sides ) or

the 36 " ?

Thank you
 
Sorry about that.

Research shows it's " dedicated " space and it the footprint of the equipment
As you were.
 