E elec_eng Senior Member Dec 9, 2008 #1 I have a 2000A (227/480V) swtchgear(dead front) one side and 200A 120/208V panels the other side of electrical room. Is this condition 3? Or condtion 2 since there is no exposed live part?
I have a 2000A (227/480V) swtchgear(dead front) one side and 200A 120/208V panels the other side of electrical room. Is this condition 3? Or condtion 2 since there is no exposed live part?
ron Senior Member Location New York, 40.7514,-73.9925 Dec 9, 2008 #2 If their working space is opposite each other, then condition 3
ivsenroute Senior Member Location Florida Dec 9, 2008 #3 IMO Yes, 4' minimum clear distance. (227/480)?