In an existing installation, a 4160 VAC 2-section Metal Clad Switchgear has 42" working clearance to a grounded wall in the rear. Switchgear contains generator breaker/protective relaying/transformer protection for a distributed generation facility. I originally thought this was a violation of Table 110.34(A) condition 2 which would require 5 ft of clearance, but I am assuming they must have used the exception since the rear sections contain no "adjustable or renewable parts). However, when the exception refers to 'all connections are accessible from locations other than rear' - what connections is this referring to - switch/relay/fuse/component connections? Or field conductor terminations? Because the 4160 field terminations are located in the rear, which would make this install a violation of 110.34. (2014 code).
If the gear is not going to be inspected/maintained while energized, does 110.34 even apply? Likewise, does the requirement in 110.33(A) apply?
The existing gear in question is crammed into a tight space, and customer wants to add a section - I am just trying to determine whether the existing is even allowed.
If the gear is not going to be inspected/maintained while energized, does 110.34 even apply? Likewise, does the requirement in 110.33(A) apply?
The existing gear in question is crammed into a tight space, and customer wants to add a section - I am just trying to determine whether the existing is even allowed.