For depth of working space, if 277V is facing 120Vis this condition 4? or 3??
Also, for a stepdown 480/208V transformer is the front considered 480V for working clearance purposes or just the side that 480V enters?
CONCUR !:thumbsup:Tricky question since you have over 150 volts to ground and under 150 volts to ground facing each other. Condition 3 only says live parts on both sides so I would say that it's condition 3. Arguably a transformer does not need to comply with 110.26 and could be treated as a grounded part.