2014 NEC. We had a discussion about working clearances related to disconnects. The language in 110.26(A) "likely to require examination, adjustment, servicing or maintenance while energized" led some of my colleagues to question the existing installation at our facility.
We have a conveyer belt system with catwalks along most of the belts, and each belt drive motor has an associated disconnect next to it mounted on the side where the catwalk is. All drives are 480V 3Ph. If it meets the requirements of 110.26(A) then 42 inches are required in front. Catwalks are only 29 inches wide. My contention was that having the disconnect precludes the motors from meeting that requirement, and the disconnect itself is not likely to require servicing so it too is code compliant as installed.
There is a large project coming up to upgrade and extend the conveyers and everyone wants to avoid a disaster in permitting if it turns out the catwalks need to be widened (would be a huge and expensive endeavor).
We have a conveyer belt system with catwalks along most of the belts, and each belt drive motor has an associated disconnect next to it mounted on the side where the catwalk is. All drives are 480V 3Ph. If it meets the requirements of 110.26(A) then 42 inches are required in front. Catwalks are only 29 inches wide. My contention was that having the disconnect precludes the motors from meeting that requirement, and the disconnect itself is not likely to require servicing so it too is code compliant as installed.
There is a large project coming up to upgrade and extend the conveyers and everyone wants to avoid a disaster in permitting if it turns out the catwalks need to be widened (would be a huge and expensive endeavor).