I am currently inspecting an 11 story building with 3 bus ducts being fed from the main gear. There are 2 2000a and 1 1600a bus ducts running through each of the small electric rooms on each floor. My interpretation of 110.26(c)(3) is that because of the size of the equipment contained in the room and the fact that each of the panels in that room will be fed from a disconnect plugged into the bus duct and the space is less than 25 ft from the doors (actual distance is less than 5 ft) the doors should be equipped with panic hardware and open in the direction of egress. The electrical engineer has responded by phone citing article 368 which covers busways, but in his opinion does not refer back to 110.26 and that the bus ducts do not contain OCP devices, switches, etc. I would appreciate some outside opinions on the interpretation.