Working Clearances

Status
Not open for further replies.

rob

Member
Location
Minnesota
I'm mounting a 200 amp panel in an electrical room (closet). I understand the 3' clearance needed in front of the equiptment, However the depth of the room (closet) is just over 2'. The GC on the job is going to install wide bi-fold doors, that when opened give me my 30" wide clearance needed, plus my 3' out front. Is this situation ok, or is 3' needed reguardless if the doors are opened or closed? Thanks guys, Rob
 

bennie

Esteemed Member
Re: Working Clearances

Only if you work in closed closets :D

[ May 28, 2003, 10:16 PM: Message edited by: bennie ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Working Clearances

Should be OK review the Art 100 definition of readily accessible and check with your AHJ.
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: Working Clearances

Just be sure that the door frame including the stops actually provides the requisite 30 inch by 78 inch opening. That usually means a minimum 32 by 80 inch nominal door frame.
--
Tom
 