Zyb Member Location Maine Occupation Design Engineer Nov 3, 2021 #1 Is there a problem here regarding on working space? i'm adding a new disconnect is a small electrical room in the basement Attachments Space.png 9.6 KB · Views: 23
Is there a problem here regarding on working space? i'm adding a new disconnect is a small electrical room in the basement
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 3, 2021 #2 What are the voltages?
W wwhitney Senior Member Location Berkeley, CA Occupation Retired Nov 3, 2021 #3 Does the plane of the face of the (N) Disconnect intersect the (E) MSP on the left? Cheers, Wayne
Zyb Member Location Maine Occupation Design Engineer Nov 3, 2021 #4 don_resqcapt19 said: What are the voltages? Click to expand... 240 volts. residential
Zyb Member Location Maine Occupation Design Engineer Nov 3, 2021 #5 wwhitney said: Does the plane of the face of the (N) Disconnect intersect the (E) MSP on the left? Cheers, Wayne Click to expand... no. MSP is about 8" from the left. disconnect is 6 depth
wwhitney said: Does the plane of the face of the (N) Disconnect intersect the (E) MSP on the left? Cheers, Wayne Click to expand... no. MSP is about 8" from the left. disconnect is 6 depth
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Nov 3, 2021 #6 Looks fine to me.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 3, 2021 #7 It's fine. If the wall opposite the disconnect were drywall then the 36" would be good even with 480 volts.
It's fine. If the wall opposite the disconnect were drywall then the 36" would be good even with 480 volts.
Zyb Member Location Maine Occupation Design Engineer Nov 3, 2021 #8 jaggedben said: Looks fine to me. Click to expand... thank you jaggedben