I am trying to determine the working space required around a 4,160V to 480V, 1,000KVA, dry type, 3-phase, transformer. The transformer will be located in a chiller building and is not acting as the service entrance. The transformer will be in a enclosure with vent openings only. So, energized parts will not be exposed.
The 2005 NEC Handbook, Table 110.34 (A) Minimum Depth of Clear Working Space at Electrical Equipment Condition 1 would seem to cover this. To me, it seems that 3 ft is the minimum clear distance required about the enlcosure.
Is this correct for my application?