mkgrady
Senior Member
- Location
- Massachusetts
Sharpie said:Have you asked your inspector about his/her stance on the issue?
That won't help me. I install starters in dozens of jurisdictions.
Sharpie said:Have you asked your inspector about his/her stance on the issue?
don_resqcapt19 said:Pierre,
Where do you draw the line? he wording of 110.26 needs some work as the existing wording prohibits the required kitchen counter receptacles as the counter is within the required work space and receptacles are equipment per Article 100.
don_resqcapt19 said:Pierre,
Where do you draw the line? he wording of 110.26 needs some work as the existing wording prohibits the required kitchen counter receptacles as the counter is within the required work space and receptacles are equipment per Article 100.
Pierre C Belarge said:I thought when I came back to this site today that this thread would have many more responses.
Shows you....you never know.:wink:
"Sufficient" being the operative word for a this "general" rule.110.26 Spaces About Electrical Equipment.
Sufficient access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
"likely to require" being the operative words...followed by the specifics (A)(1) - (3) for various conditions.110.26(A) Working Space.
Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.