Was it a requirement to have 36" working space clearance in front of electrical equipment?
And if you have the code book, I would really appreciate a copy of the section.

TIA
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The 1975 NEC had requirements similar to the current 2020 version but different distances. In 1975 it was section 110.16(a) which had for:
0-150 volts: condition 1 and 2: distance of 2.5' and condition 3: 3'.
For 151-600 volts was condition 1: 2.5', condition 2: 3.5', condition 3: 4'.
 