Need clarification for Working space of the Dry MV transformer, is it required from the body of transformer 13.8/0.4 KV, or it shall be taken from MV termination box which is exposed from the transformer body?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Need clarification for Working space of the Dry MV transformer, is it required from the body of transformer 13.8/0.4 KV, or it shall be taken from MV termination box which is exposed from the transformer body?
Working space is always considered from the outside of the enclosure.
 