in further understanding 110.26 nec. i am mounting a single phase load center to the exterior wall in a commercial building, there is a joining dry wall to my left and a gas furnace to my right with a max of 32" between the furnace and wall with plenty of depth space, would i be in violation of the 30" rule if i were to mount it in that space. (panel approx 14" wide) I was told by a AHJ that the 30" rule applied by measuring from the side of the panel to the furnace. i am confused because exhibit 110.18 of the 02 shows different. thanks for any info you can give as i am a new member here.