Working space in front of condensing units

Status
Not open for further replies.

ivsenroute

Senior Member
Location
Florida
Not enough or OK?

IMG_7166.JPG
 
It would pass where I am if it was a swap out. If it was a new install probably not.
 
I would be upset if I had to work on it. Did the mechanical cont. create this problem or did the HO just slide the condensor over? Even if they move the fuel tank you probably won't have room between the wall and the ac. That is the area that the elec. components are located.
 
Deficiency

110.26

It was an existing install moved to the right to make room for the shed on the left.

Was the A/C moved without the wiring being touched? If so, then I don't think you could cite any violation of the disconnect.


And...110.26(A) has been argued many many times here.

Is the Disconnect "...likely to require examination, adjustment, servicing, or maintenance while energized..."?
The Disconnect, not the A/C.
Shouldn't it be de-energized before performing any of those actions to the Disconnect?
 