I'm looking at a situation where I have a pad mount MV metering cabinet with the CT/PTs in the rear compartment, and the meters are installed inside the dead-front compartment. In front this enclosure on the same pad is another piece of equipment.
What should the working clearance be? We are looking at this as Condition 3, voltage coming into the metering cabinet is 12.47kV.
I have two conflicting interpretations in Art. 110 regarding the minimum working clearances and am looking for clarification.
Interpretation #1
9' required as the highest voltage in the equipment is 12.47kV.
Interpretation #2
5' required as the voltage on the exposed side is <600V. Since there is isolation between the 12.47kV section and the dead-front compartment, we are allowed to use the lower voltage ratings to determine working clearances.
Thanks!
Michael