Working Space Requirements for Non-power Panels

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The AHJ is correct.

There is nothing that suggests the rule only applies to power panels, and the voltage in Table 110.26(A)(1) starts at zero.
In addition the parent text in 110.26 says "all electrical equipment".
 