Hello forum!
I am inspecting an area that contains several individually cooled 480V VFD cabinets. The (4) cabinets are being placed on an equipment pad in the center of a process building. The arrangement is laid out so that there are 2 sets of back to back cabinets, and in the center of the 2 groups, 2 of the cabinets face each other.... basically creating "Condition 3" on Table 110.26(A)(1), so since both opposing cabinets operate at 480v, there is a working space requirement of 4 feet.
This is where I need help... Both opposing VFD cabinets have double swinging doors. Are these doors allowed to encroach upon the 4 foot working space of the opposite cabinet, or does spacing need to be such that the doors stay out of the working space? I.e. Swing of the door plus 4 foot.
Also keep in mind that the doors swing beyond 90 degrees, effectively shortening their amount of encroachment. (not sure if that matters).
Any help/opinions.
I am inspecting an area that contains several individually cooled 480V VFD cabinets. The (4) cabinets are being placed on an equipment pad in the center of a process building. The arrangement is laid out so that there are 2 sets of back to back cabinets, and in the center of the 2 groups, 2 of the cabinets face each other.... basically creating "Condition 3" on Table 110.26(A)(1), so since both opposing cabinets operate at 480v, there is a working space requirement of 4 feet.
This is where I need help... Both opposing VFD cabinets have double swinging doors. Are these doors allowed to encroach upon the 4 foot working space of the opposite cabinet, or does spacing need to be such that the doors stay out of the working space? I.e. Swing of the door plus 4 foot.
Also keep in mind that the doors swing beyond 90 degrees, effectively shortening their amount of encroachment. (not sure if that matters).
Any help/opinions.