110.26(A)(3) Height of Working Space - verses - 110.26(E)(1)(b) Dedicated Equipment Space. Let me start off by saying I realize one section is for working space and the other is dedicated space. 110.26(E)(1)(b) Foreign Systems are permitted if protection is provided….This seems to conflicting with 110.26(A)(3). Here is the question finally. We have some fire alarm above a panelboard. For the purpose of this question it’s a 4” square box that may have a device. If it’s a violation we will blank it off…but even if blanked off is it still a violation of 110.26(E)(1)(b) that does not mention foreign systems? Thanks