Can multiple disconnects occupy the same 30 in space. The NEC HB said they can overlap but, is there a min space between each required? Also can a 6 foot wall have 4 or 5 lighting panels mounted side by side?
 
Re: Working space

I don't believe space is required between enclosures unless the instructions for one reqiure there to be. Also, proper operation of the enclsoure (operation of switches, taking of the cover, etc..) must be maintained.

Without knowing more about the room,space, and specific conditions, I don't see any reason why 4 or 5 panels can't be mounted side by side.
 