We are in the starting phase (fondations will be poured mid-November) of a new control building in our refinery. The proposed location of the building's 500kva transformer (along with a 500kw generator) will be set on a dedicated area outside of the building. This area is at the same elevation as the fondation of the control building. However, the access to the transformer's termination chamber (4160v/480v)is 18" from the outside edge of this slab. This area will have a handrail around the edge due to grade at this location will be 3 feet 6 inches lower than the top of the building floor & the bottom of the transformer.
Per NEC's Article 110.26, the mininum working space for equipment (depending on the voltage) is 30" wide or the width of the equipment with a mininum depth in front of the equipment of 36". Engineering is proposing to delete the handrail in the area of the termination compartment to comply with 110.26 & the 90 degree rule for electrical equipment doors (the doors open toward the handrail).
Engineering's position is, removal of the handrail will comply with the NEC's requirements. The equipment is low maintenance & the transformer can be serviced with scaffold erection each time.
Is there anything in the NEC requiring this maintenance work space to be 30" X 36" at the same elevation?
Per NEC's Article 110.26, the mininum working space for equipment (depending on the voltage) is 30" wide or the width of the equipment with a mininum depth in front of the equipment of 36". Engineering is proposing to delete the handrail in the area of the termination compartment to comply with 110.26 & the 90 degree rule for electrical equipment doors (the doors open toward the handrail).
Engineering's position is, removal of the handrail will comply with the NEC's requirements. The equipment is low maintenance & the transformer can be serviced with scaffold erection each time.
Is there anything in the NEC requiring this maintenance work space to be 30" X 36" at the same elevation?