hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch shows electrical room with 800A meter stack with 800A main breaker.
Its 208V three phase. The electric room is going to be brand new and its at plan review stage.
I was wondering does would condition #1 exposed live parts one side and no live or grounded parts on table 110.26(A)(1) would apply where in sketch it is shown 16 inches or any other rule in NEC 2017 apply So basically their one would have to provide 3 feet clearance instead of 16 inches. Can anyone know or help?
Its 208V three phase. The electric room is going to be brand new and its at plan review stage.
I was wondering does would condition #1 exposed live parts one side and no live or grounded parts on table 110.26(A)(1) would apply where in sketch it is shown 16 inches or any other rule in NEC 2017 apply So basically their one would have to provide 3 feet clearance instead of 16 inches. Can anyone know or help?