A Akten Member Location New York Occupation Engineer Jul 1, 2025 #1 Hi, does if an electrical equipment is installed in a room with drywall/sheetrock/gypsum board wall with metal studs, does this meet requirement for Condition 1 working space per NEC 110.26 and 110.34?
Hi, does if an electrical equipment is installed in a room with drywall/sheetrock/gypsum board wall with metal studs, does this meet requirement for Condition 1 working space per NEC 110.26 and 110.34?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 1, 2025 #2 Yes drywall is not considered to be a grounded surface like concrete, tile, etc.