I don't see where you are getting 40 inches from.
If no grounded parts on opposite side of working space minimum clearance is 3 feet for all three conditions (assuming your 208 volts you mention means 120/208). Table 110.26 A 1 is based on voltage to ground. You do need to have the door at least 30 inches wide or equipment width whichever is greater if the closet does not provide 36 inches in front of the equipment - and that may be subject to interpretation by some AHJ's.
The applicable Condition will not depend on the characteristics of the door, but rather on whatever type of surface is behind you, as you stand in the open doorway looking at the gear. The doors are not relevant.. . . the question is if there is a door in front of said gear or panel does condition 2 or any conditon apply..
Concrete, brick or tile is considered grounded structures so condition 2 applies not condition 1, the question is if there is a door in front of said gear or panel does condition 2 or any conditon apply..
Concrete, brick or tile is considered grounded structures so condition 2 applies not condition 1, the question is if there is a door in front of said gear or panel does condition 2 or any conditon apply..
Yes but if you just have 120/208V panels than your nominal voltage to ground is only 120V, leaving your minimum clear distance at 36 inches. (0-150V)
I don't see where you are getting 40 inches from.
If no grounded parts on opposite side of working space minimum clearance is 3 feet for all three conditions (assuming your 208 volts you mention means 120/208). Table 110.26 A 1 is based on voltage to ground. You do need to have the door at least 30 inches wide or equipment width whichever is greater if the closet does not provide 36 inches in front of the equipment - and that may be subject to interpretation by some AHJ's.