In EC&M's magazine this month, there's an article "The Case of the Exploding Chain Saw" that talks about an accident with an electrician that was doing work in an electrical closet, which was used for storage. The author says that using an electrical closet for storage is not a code violation but a good practice not to do so as noted in 110.26(B).
But, 110.26(B) says this:
"Working space required by this section shall not be used for storage. When normally enclosed live parts are exposed for inspection or servicing, the working space, if in a passageway or general open space, shall be suitably guarded."
So isn't this a code requirement??
BTW, the article is really sad. It turns out an experienced electrician got an arc blast from a chainsaw used as storage that hit a busbar of 277/480 panel. He lost his short term memory, requires long term rehab, and became divorced...
But, 110.26(B) says this:
"Working space required by this section shall not be used for storage. When normally enclosed live parts are exposed for inspection or servicing, the working space, if in a passageway or general open space, shall be suitably guarded."
So isn't this a code requirement??
BTW, the article is really sad. It turns out an experienced electrician got an arc blast from a chainsaw used as storage that hit a busbar of 277/480 panel. He lost his short term memory, requires long term rehab, and became divorced...