From the 2008 ROP
1-99 Log #691 NEC-P01 Final Action: Reject
(110.26)
_____________________________________________________________
Submitter: Timothy Schultheis, H.F.Lenz Company
Recommendation: Revise as follows:
11 0.26 Spaces About Electrical Equipment. Sufficient access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operations and maintenance of such equipment. Enclosures housing electrical apparatus that are controlled by a lock(s) shall be considered accessible to qualified persons. Where the entrance has a personnel door(s), the door(s) shall open in the direction of egress, or while open, not interfering with working spaces .
Substantiation: Please see the diagrams that I have provided.
Note: Supporting Material is available for review at NFPA headquarters.
Panel Meeting Action: Reject
Panel Statement: Section 11 0.26 is a general statement regarding working spaces about electrical equipment. There is no mention in this section of an
entrance, so the proposed language would be out of place in the paragraph. CMP-1 refers the submitter to NEC Section 11 0.26(C)(1) as it requires at least one entrance to working space. Additionally, the proposed language currently exists in Section 11 0.26(C)(2) for large equipment and repeating the text would cause confusion and conflict. CMP-1 appreciates the diagrams submitted and understands the concerns, but notes that the scenarios presented are work practice issues too. Adding specific requirements to all entrances to working spaces will not prevent poor work practices.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12