I was always under the impression that disconnects had to comply with 110.26. Anybody have any input on that.
Only the equipment that is likely to require maintenance or servicing. IMO, a disconnect would not.
Only the equipment that is likely to require maintenance or servicing. IMO, a disconnect would not.
110.26 Spaces About Electrical Equipment.
Sufficient access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
(A) Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.
What about examination (testing)?
What about examination (testing)?
That only works if you turn it off on the line side of the disconnect....if you don't it is still live.Turn it off, connect the test equipment, turn it back on, turn it off to remove the test equipment. Nothing to it
That only works if you turn it off on the line side of the disconnect....if you don't it is still live.
That only works if you turn it off on the line side of the disconnect....if you don't it is still live.
That has nothing to do with the code rule. Even with that procedure, the equipment is being tested while live and 110.26(A) space is required. It is my opinion that ALL electrical equipment is likely to be tested while energized.I work with several companies that require the service tech to turn off the supply to any disconnect then attach any testing equipment then turn the supply to that disconnect back on in order to safely do voltage testing to the line side of the disconnect.
Again that has nothing to do with the application of the NEC rule. The fact that you are using the correct PPE does not change the code requirement to provide workspace for all electrical equipment that may be tested while energized.110.26 is not a rule to allow people to test for voltage in an unsafe manner. 110.26 does not relieve the requirement for the proper type and category rated meter or the proper PPE before doing a voltage test. The unsafe manner in which we do things is not covered by the NEC.
That is not what I said. I said that you cannot install the code required kitchen counter top receptacle without creating a violation of 110.26.As you pointed out the disconnect over a kitchen countertop does not have to meet 110.26 and I bet there has been many that has tested for voltage on one of those.
That is not what I said. I said that you cannot install the code required kitchen counter top receptacle without creating a violation of 110.26.
"Receptacle. A receptacle is a contact device"
Receptacle. A receptacle is a contact device installed at the
outlet for the connection of an attachment plug. A single
receptacle is a single contact device with no other contact
device on the same yoke. A multiple receptacle is two or
more contact devices on the same yoke.
Device. A unit of an electrical system that carries or controls
electric energy as its principal function.
Equipment. A general term, including fittings, devices, appliances,
luminaires, apparatus, machinery, and the like used as a
part of, or in connection with, an electrical installation.